Diagnosing the Performance Gap Between Design and Operational Energy Use Getting to Zero Forum October 10, 2019
Authored By: Commissioned By:
Higher Efficiency Lower Efficiency
...or so we thought…
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs
1 10/15/2019
Lower Energy Higher Energy
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs
The “Performance Gap”
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs
2 10/15/2019
APPROACH Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 5
A QUICK LOOK AT OUR DATA – Multi-Unit Residential.
Suite Level Meters Utility Bills 83 BUILDINGS 43 BUILDINGS
Design Models 95 BUILDINGS Modelled & Metered Data 19 BUILDINGS
End Use Meters and Models 6 BUILDINGS
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 6
3 10/15/2019
Multi-Unit Residential KEY FINDINGS
RECENT MODELLED PERFORMANCE OF DESIGN STAGE MURBS IN TORONTO TGSv3 OBC Tier 1 2012 12
Minimum Maximum (120 ekWh/m2/year) (410 ekWh/m2/year) 10
8 Meet 2012 Ontario Building Code Min. Performance Only 5 Meet TGS Tier 1 EUI target buildings met 6 all three targets for 4 TGS Tier 1 Number of Buildings
2
0 70 - 80 - 70 90 - 80 90 - 100 - 90 320 -330 320 100 - 110 100 - 130 120 - 140 130 - 150 140 - 160 150 - 170 160 - 180 170 - 190 180 - 200 190 - 210 200 - 220 210 - 230 220 - 240 230 - 250 240 - 260 250 - 270 260 - 280 270 - 290 280 - 300 290 - 310 300 - 320 310 - 340 330 - 350 340 - 360 350 - 370 360 - 380 370 - 390 380 - 400 390 - 410 400 110 - 120 - 110
EUI (ekWh/m2) MODELLED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 8
4 10/15/2019
ENERGY USE INTENSITIES PER METERED DATA FROM BUILDINGS BUILT BETWEEN 1995 AND 2015.
Fan Coil Unit WSHP 35 350 WSHP Median – 30 300 FCU Median – 235 ekWh/m2 2 243 ekWh/m 25 250 20 200
15 150 EUI (ekWh/m2/yr) EUI 100 10
50 5
0 0
FCU - Elec FCU - Gas WSHP - Elec WSHP - Gas
FCU – Fan Coil Unit WSHP – Water Source Heat Pump METERED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 9
COMPARING METERED ENERGY USE INTENSITY AGAINST CALIBRATED ENERGY MODELS On average, the studied multifamily 300 buildings used just 13% more energy than modeled. But that’s 25 250 not the full story.
20 200
15 150 EUI EUI EUI EUI (ekWh/ft2/yr) (ekWh/m2/yr) 10 100
50 5
0 0 EUI - Billed EUI - Caibrated Model
MODELLED + METERED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 10
5 10/15/2019
PERFORMANCE GAP BY END USE – METERED VS. MODELLED ENERGY USAGE.
75 39% Median Metered
Median Modeled % 50 -26 “Performance Gap” 2 21% ekWh / m
25 % 61% 0 % 13 94% -26% 61% 46% 0
MODELLED + METERED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 11
PERFORMANCE GAP - SPACE HEATING. Modelled gas usage for space heating is 39% lower than metered performance
120 Fan Coil Unit WSHP
10 100
8 80
6 60 EUI (ekWh/m2)yr) 4 (ekWh/ft2/yr) EUI 40
20 2
0 0 Metered EUI Modelled EUI MODELLED + METERED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 12
6 10/15/2019
SPACE HEATING – EFFECTS OF THERMAL BRIDGING.
100 Building A Building B 9 90 8 80 7 70 6 60 5 50
4 40
3 EUI (ekWh/ft2/year) 30
20 2
10 1
0 0 Original R Value Updated R Value Original R Value Updated R Value Modelled EUI Metered EUI Re-modeled EUI MODELLED + METERED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 13
SPACE HEATING – INFILTRATION.
Model/Code Default Values Measured Values in Constructed Bldgs 0.6
0.5 ) 2
/ft 0.4 Mean 0.38 50 2 cfm50/ft
0.3 Mean 0.21 2 cfm50/ft 0.2 Infiltration Rate (cfm
0.1
0 EE4 eQuest NECB PassivHaus US Army Toronto Toronto Toronto Seattle Data Corps of MURB Data MURB Data MURB Data Base*** Engineers Base 2013 Base 2013 Base 2015** (All)* (2000 + Newer)*
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs Sidewalk Labs MURB Study / 14
7 10/15/2019
PERFORMANCE GAP – DOMESTIC HOT WATER. Modelled gas usage for domestic hot water production varied from 44% lower to 14% higher than metered performance, with a median of 21% lower
70 Fan Coil Unit WSHP
6 60
5 50
4 40
3
EUI(ekWh/m2/yr) 30 EUI (ekWh/ft2/yr) EUI
2 20
10 1
0 0
Metered EUI Modelled EUI MODELLED + METERED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 15
PERFORMANCE GAP – IN-SUITE ELECTRICITY. Modelled in-suite electricity usage is 26% higher than metered performance
60 Fan Coil Unit WSHP
5 50
4 40
3 30 EUI (ekWh/ft2/yr) EUI EUI(ekWh/m2/yr) 2 20
10 1
0 0 Metered EUI Modelled EUI MODELLED + METERED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 16
8 10/15/2019
IN-SUITE ELECTRICITY – AGGREGATE DATA. Data pulled from 80 Toronto MURBs, constructed between 2000-2015, shows actual suite electricity is lower than modeled. Mean Modelled Mean 3,800 kWh/year 2,900 3500 kWh/year
3000 MODELLING 30% Difference 2500 PRACTICES
Models assume default 2000 power densities, expressed per area of floor space, and 1500 default usage schedules. Number of Suites 1000 Current code requirements use default power densities from 1997. 500
0
Assumed to be Annual Electricity Usage (kWh) Partially Unoccupied MODELLED + METERED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 17
PERFORMANCE GAP – MISC COMMON AREA ELECTRICITY. Modelled common area electricity usage is 94% lower than metered performance
40 Fan Coil Unit WSHP 3.5 35 3.0 30
2.5 25
2.0 20 EUI (ekWh/ft2/yr) EUI EUI(ekWh/m2/yr) 1.5 15
1.0 10
5 0.5
0 0.0 Metered EUI Modelled EUI
MODELLED + METERED
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 18
9 10/15/2019
MULTI UNIT RESIDENTIAL- KEY FINDINGS
Only 5% of Toronto MURB projects in design and construction would meet 1. TGSv3, Tier 1
Toronto MURBs use 13% more energy and emit 28% more GHG emissions 2. than predicted by modelling. Bigger gaps by end use: 3. • Space Heating- + 39% • Domestic Hot Water +21% • Baseload Electricity +94% • Suite Electricity -26%
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs / 19
Managing the Performance Gap
Outcome-Based Code Dynamic building control Dynamic and responsive Smart home control that with dynamic targets to reflect actual and tenant space control that learns tenant preferences normalized by building predicted occupancy, includes plug loads and and responds to price occupancy, weather and weather and tenant thermostats tenant energy use feedback
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs
10 10/15/2019
Tool to enable Outcome Based Energy Codes
A real time normalization of Toronto Green Standard or Passive House-like energy and GHG-intensity budgets based upon: • Building occupancy • Weather • Productive tenant energy use
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs
Autonomous Building tools to weed out the electricity use no one cares about or that actually degrades comfort, like overheating and air-conditioning
Home Scheduler - automation to provide a predictable utility bill
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs
11 10/15/2019
Autonomous Building tools to weed out the electricity use no one cares about or that actually degrades comfort, like overheating and air-conditioning
Home Scheduler - automation Office Scheduler - automation to enhance to provide a predictable utility bill comfort and eliminate energy waste
Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs
Autonomous Building tools to weed out the electricity use no one cares about or that actually degrades comfort, like overheating and air-conditioning
Home Scheduler - Office Scheduler - automation to enhance automation to provide a comfort and eliminate energy waste predictable utility bill Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs
12 10/15/2019
Autonomous Building tools to weed out the electricity use no one cares about or that actually degrades comfort, like overheating and air-conditioning
Home Scheduler - automation Office Scheduler - automation to Building Operator Scheduler - dynamic to provide a predictable utility enhance comfort and eliminate energy building control that responds to tenants bill waste Urban Equation, EQ Building Performance, Energy Profiles Limited, Sidewalk Labs